Controller CLARE 5:
Controller CLARE 5

Jumpers on the board

  

 

 

Inputs and outputs on the processor board of the controller can be configured. The input marked TC (clamps C11, C12) is a fixed thermocouple, while the second input AI2 can be set as thermocouple, voltage or current. Both outputs AO1 and AO2 they can be configured as voltage or current. The basic configuration includes two thermocouple inputs and two voltage outputs. In the following jumper overview, the default configuration is highlighted in bold.

 

JP1

upper jumper - current output AO1

lower jumper - voltage output AO1

JP2

Reserved - no function
Standard settings -right jumper

JP3

upper jumper - voltage output AO2

lower jumper - current output AO2

JP4

upper jumper - current output AO2

lower jumper - voltage output AO2

JP5

connected - voltage input 0 - 10 V

disconnected - thermocouple or current input 4 - 20 mA

JP6

connected - current input 4 - 20 mA

disconnected - thermocouple or voltage input 0 - 10 V

JP7

connected - thermocouple or current input 4 - 20 mA

disconnected - voltage input 0 - 10 V

JP8

connected - current input 4 - 20 mA or voltage input 0 - 10 V

open - thermocouple input

JP9

upper jumper - voltage output AO1

lower jumper - current output AO1

 

Default jumper configuration on the processor board are highlighted in bold.

 

INPUT

TYPE

JP5

JP6

JP7

JP8

TC (AI1)

thermocouple

-

-

-

-

AI2

thermocouple

X

X

S

X

voltage

S

X

X

S

current

X

S

S

S

X - disconnected, S - connected

 

EXIT

TYPE

JP1

JP3

JP4

JP9

AO1

voltage

D

-

-

H

current

H

-

-

D

AO2

voltage

-

H

D

-

current

-

D

H

-

D - lower jumper, H - upper jumper