The CLARE 5 controller has terminal blocks on the back for connecting power, communication, inputs and outputs. Depending on the hardware configuration of the controller, 10 to 36 contacts are available. The minimum controller configuration is colored blue. In case the controller uses a LAN module (Ethernet), are terminals C1 to C4 replaced by a standard RJ-45 connector to connect to the network.
Terminal block on the source board:
Clamp |
Designation |
Description |
A1, A2 |
R5 |
Switching relay No. 5 (3 A / 240 V) |
A3, A4 |
R4 |
Switching relay No. 4 (3 A / 240 V) |
A5, A6 |
R3 |
Switching relay No. 3 (3 A / 240 V) |
A7, A8 |
R2 |
Switching relay No. 2 (3 A / 240 V) |
A9, A10 |
R1 |
Switching relay No. 1 (3 A / 240 V) |
A11 |
L |
Phase wire 230V for powering the controller |
A12 |
N |
Neutral wire for powering the controller |
Terminal blocks on the processor board:
Clamp |
Designation |
Description |
C1 |
Ter |
Terminator for RS-485 line. Connect to terminal C2 if it is to be used |
C2, C3 |
485 |
RS-485 communication line (C2 = B wire, C3 = A wire) |
C4 |
_|_ |
Grounding of the communication RS-485 line |
C5, C6 |
AO2 |
Universal analog output #2 (C5 +, C6 -) |
C7, C8 |
AI2 |
Universal analog input #2 (C7 +, C8 -, max. 10 V) |
C9, C10 |
AO1 |
Universal analog output #1 (C9 +, C10 -) |
C11, C12 |
TC |
Thermocouple input (C11 +, C12 -) |
Terminal blocks on the expansion board:
Clamp |
Designation |
Description |
B1 |
DI2 |
Digital input #2 |
B2 |
_|_ |
Grounding for digital inputs |
B3 |
DI1 |
Digital input #1 |
B4 |
_|_ |
Grounding for digital inputs |
B5, B6 |
AO4 |
Universal analog output #4 (B5 +, B6 -) |
B7, B8 |
AI4 |
Universal analog input No. 4 (B7 +, B8 -, max. 10 V) |
B9, B10 |
AO3 |
Universal analog output #3 (B9 +, B10 -) |
B11, B12 |
AI3 |
Universal analog input No. 3 (B11 +, B12 -, max. 10 V) |